anyone know about heating systems in houses?
it's a tankless heat/hotwater system with the huge radiators{the big square ones}closed system.
i'm bleeding the air out of all the radiators.{due to a baseboard add on earlier in the spring}
do i have to add water somewhear??????to the system??????
it's got tons of air in it.
the two radiators on the top floor are cold as ice.
downstairs ones are kickin.
thanks for any help.
it's an old house 
mike
|
|
|
|
11-16-2004, 09:32 PM
|
#2
|
Registered User
Join Date: Nov 2003
Location: West Wareham
Posts: 1,189
|
FF there should be a fast fill on your bioler, it is hard to describe it has a square base maybe 3" x3" square and on the top is a lever that you can lift this will add water but you do not want your pressure to go up higher than 20 psi your PRV will pee off the overpressure, you need to make sure your zones are open when you add water one at a time however make sure the power is off you will smoke the zone valves by manually opening them with power on, this is also how your purge your system of air just add a hose and let the air and water run in one side out the other
|
|
|
|
11-16-2004, 09:40 PM
|
#3
|
"Fishbucket"
Join Date: Feb 2004
Location: Bahston Hahbah
Posts: 6,588
|
thanks,
back to the basement.
it's ony one zone for the whole house.
|
|
|
|
11-16-2004, 09:44 PM
|
#4
|
Really Old & Really Grumpy
Join Date: Jun 2002
Location: not a clue
Posts: 4,860
|
one zone  how come 
|
BOAT fish do count.
|
|
|
11-16-2004, 09:57 PM
|
#5
|
"Fishbucket"
Join Date: Feb 2004
Location: Bahston Hahbah
Posts: 6,588
|
whell i think it's one zone.
i can't shut any one room down unless i turn off the valves on the radiators.
here's what i found.
the pressure is down about 7 psi.
i found the piramid shaped valve to let water in.
i opened it bout ten/15 seconds, no psi change, ran upstairs three rads are filled w/ airlike never before ppppsshhhhhhh!!!!!!!!!!!!!. top floor two got nuthin, no air no water no nuthing.
do i let the water in the valve with the very top floor radiator bleeder open?
while i'm in the basement?
there is another bleeder near the burner, but litle air comes out.
|
|
|
|
11-16-2004, 10:33 PM
|
#6
|
BigFish Bait Co.
Join Date: Apr 2003
Location: Hanover
Posts: 23,392
|
Turn your heat up....bleed the air from the radiators from the closest to the boiler to the one furthest away! Make sure your water level is where it is supposed to be at the boiler....do you have one of those site glasses where you can read the water level? 
|
Almost time to get our fish on!!!
|
|
|
11-16-2004, 10:55 PM
|
#7
|
Registered User
Join Date: Jul 2002
Location: Maine
Posts: 4,547
|
Ditto what Larry said. I have radiators in my house and they make lots of noise when the water runs low.
|
|
|
|
11-16-2004, 11:02 PM
|
#8
|
"Fishbucket"
Join Date: Feb 2004
Location: Bahston Hahbah
Posts: 6,588
|
tahhh dahhh!!!!
i fixed it!!!!
thanks guys!!
scratch one more from the honey-do list
there was tons of air in there!
lots of noise too.
i opened the water in--> valve till 20 psi, ran upstairs bled from lowest level to top. then back to the basement to raise the pressure again, then back upstairs for the very top floor. and voila' water now comes out.
back to the basement, raised the pressure back to 20 psi, and the whole house is toasty warm, and no more creeks either.
thanks again  i knew i would find out here
should i keep it at 20 psi?
mike
Last edited by thefishingfreak; 11-16-2004 at 11:18 PM..
|
|
|
|
11-16-2004, 11:52 PM
|
#9
|
Finally
Join Date: Jan 2003
Location: FL
Posts: 7,181
|
Cool Mike, at least u got somethin accomplished besides fishing. How dem Cod doin? I'm ready when u are.
|
F-18®
It IsWhat It Is
¸.·´¯`·.¸><((((º>¸.·´¯`·.¸><((((º>¸.·´¯`·.¸><((((º >¸.·´¯`·.¸><((((º>¸.·´¯`·.¸><((((º>¸.·´¯`·.¸><(((( º>
|
|
|
11-16-2004, 11:57 PM
|
#10
|
"Fishbucket"
Join Date: Feb 2004
Location: Bahston Hahbah
Posts: 6,588
|
this weekend looks very nice 
if you can get russ outta bed, he knows the route.
boats in,,,,, might as whell go for a ride 
|
|
|
|
11-16-2004, 11:59 PM
|
#11
|
Finally
Join Date: Jan 2003
Location: FL
Posts: 7,181
|
Get Russ out of bed? LOL. I'll try. 
|
F-18®
It IsWhat It Is
¸.·´¯`·.¸><((((º>¸.·´¯`·.¸><((((º>¸.·´¯`·.¸><((((º >¸.·´¯`·.¸><((((º>¸.·´¯`·.¸><((((º>¸.·´¯`·.¸><(((( º>
|
|
|
11-17-2004, 04:56 AM
|
#12
|
New (used) boat!!!!
Join Date: May 2003
Location: Goshen,CT
Posts: 315
|
Isn't this a great group!!! From Bass to boilers....and most things in between....ya get answers!!
FF- Thats one of the best signature lines I have seen.
Brandon
|
***** I WOULD STILL RATHER GO HUNTING W/ #^^^^& CHENEY  THAN GO FOR A DRIVE W/ TED KENNEDY  ******
|
|
|
 |
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
All times are GMT -5. The time now is 03:23 AM.
|
| |